[Che-student-staff-list] FW: FRNY Manifold/Air shutdown

Valley, Jeffrey L valley at purdue.edu
Mon Jun 19 13:56:51 EDT 2023


BE ADVISED - This Thursday 6-22-23, all fume hoods on the addition side of the building will be shut down for work to be performed on the control panels. Please read the emails below that explains the procedures that need to be followed for this shut down. If you have any questions please contact me.
Thank you.

Jeff Valley

From: Bentley, Heath E <hebentle at purdue.edu>
Sent: Monday, June 19, 2023 9:14 AM
To: Jewell, Patrick R <prjewell at purdue.edu>; Valley, Jeffrey L <valley at purdue.edu>
Cc: Butt, Eric M <embutt at purdue.edu>; Wallar, Brian G <wallarb at purdue.edu>; Wilson, Zachary R <wilsonz at purdue.edu>; Ridgway, Robin M <rmridgway at purdue.edu>; Juristyarini, Pramitha <pjuristy at purdue.edu>
Subject: RE: FRNY Manifold/Air shutdown

Jeff and Patrick,

I've attached the standard operating procedure and shut down notices for servicing lab exhaust systems. It may be necessary to share this with siemens as well. Here are a couple of key things to note from the SOP;


  *   PF and building deputy will communicate/coordinate with the labs and lab PIs the need for service and the duration of the fan shut down.

  *   Except for emergency situations, PF personnel will post the "Shut Down Notice" on the affected chemical fume hood(s) a minimum of three days prior to the scheduled shut down. The notice should be posted in the lower, center area of the sash so that it is easily visible. The affected hood(s) will be out of service during the period indicated on the notice regardless of whether or not the fan is actually operating. If the exhaust system being serviced provides ventilation for an entire room, the "Shut Down Notice" should be placed on the door to the room.
  *   The laboratory PI must ensure and sign off on the "Shut Down Notice" that hazardous materials have been secured, the sash remains closed and no operations/experiments, including closed systems, shall be conducted in the chemical fume hood(s) for the duration of the maintenance as indicated on the posted notice.
  *   PF personnel will verify that all chemicals and equipment have been secured or removed from the hood and the Laboratory Personnel section of the "Shut Down Notice" has been completed before maintenance work begins.

Let me know if you have any questions or concerns.

Thanks,

Heath Bentley, MS
Industrial Hygienist |  Environmental Health and Safety / REM*
hebentle at purdue.edu<mailto:hebentle at purdue.edu> | 765-494-3134
550 Stadium Mall Drive
West Lafayette, IN 47907
https://www.purdue.edu/ehps/rem
[3F65CD]<https://www.purdue.edu/?utm_source=signature&utm_medium=email&utm_campaign=purdue>
*Radiological and Environmental Management (REM) is changing our name.  We will now be Environmental Health and Safety (EHS)

From: Jewell, Patrick R <prjewell at purdue.edu<mailto:prjewell at purdue.edu>>
Sent: Monday, June 19, 2023 8:33 AM
To: Valley, Jeffrey L <valley at purdue.edu<mailto:valley at purdue.edu>>
Cc: Butt, Eric M <embutt at purdue.edu<mailto:embutt at purdue.edu>>; Bentley, Heath E <hebentle at purdue.edu<mailto:hebentle at purdue.edu>>; Wallar, Brian G <wallarb at purdue.edu<mailto:wallarb at purdue.edu>>; Wilson, Zachary R <wilsonz at purdue.edu<mailto:wilsonz at purdue.edu>>; Ridgway, Robin M <rmridgway at purdue.edu<mailto:rmridgway at purdue.edu>>
Subject: FRNY Manifold/Air shutdown

Jeff,

The siemens contractor is requesting a shutdown this Thursday, June 22nd. This would take down the fume hoods on the newer side of Forney and HVAC supply air would be backed down to prevent damage to the roof and also keep egress in and out of laboratory doors possible.

I have copied EHS for awareness.

Patrick Jewell
Zone Leader | Operations and Maintenance
PSYC B110 | 703 Third Street | West Lafayette, IN 47907
o: 765-494-1773<tel:7654941773>
m: 765-430-3614<tel:7654303614>
prjewell at purdue.edu<mailto:prjewell at purdue.edu>
[cid:image003.png at 01D9A28C.A6F8BAA0]<https://www.purdue.edu/>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: </ECN/mailman/archives/che-student-staff-list/attachments/20230619/12ead409/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 4389 bytes
Desc: image002.jpg
URL: </ECN/mailman/archives/che-student-staff-list/attachments/20230619/12ead409/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 10125 bytes
Desc: image003.png
URL: </ECN/mailman/archives/che-student-staff-list/attachments/20230619/12ead409/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Servicing Laboratory Exhaust Systems SOP.DOCX
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 40959 bytes
Desc: Servicing Laboratory Exhaust Systems SOP.DOCX
URL: </ECN/mailman/archives/che-student-staff-list/attachments/20230619/12ead409/attachment-0001.docx>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Shut Down Notice.pptx
Type: application/vnd.openxmlformats-officedocument.presentationml.presentation
Size: 100085 bytes
Desc: Shut Down Notice.pptx
URL: </ECN/mailman/archives/che-student-staff-list/attachments/20230619/12ead409/attachment-0001.pptx>


More information about the Che-student-staff-list mailing list