[Bnc-facility-notice] NOTICE - East General Lab Wing HVAC Interruption - Update

Voorhis, Mark L. mvoorhis at purdue.edu
Fri Dec 18 17:20:24 EST 2020


Dear East Lab Wing Users,

Early this morning there was a building controls alarm from the east wing HVAC unit.  After investigation there was a failure of the fan motor electrical control system.  The electrical controls to the fan motor are obsolete with no technical support or spare parts available.  PUPF is working on ordering replacement parts today, but with the timing of the failure with fan motor controls it will not be fixed during the Purdue campus holiday closure.

With the rising number of COVID cases and the reduced number of air changes, REM has given the direction to close all chemical and biological labs until the HVAC system is fully repaired.  However dry labs will remain open with a reduced number of air changes so you can continue working but at your own risk.

The following dry labs will be open during the holiday break but all other labs will posted closed until future notice.

Open Dry Labs
1031
1045
1083
1077
2037
1089

Closed Biological & Chemical Labs
1039
2031
1043
2037
1066
2043
1081
2077
2081
2087
2087A
2087B

We are sorry for this unscheduled interruption but PUPF and Operation & Maintenance department are working on the issues the best they can.

Best Regards,

Mark Voorhis
Building Manager
Purdue University
Birck Nanotechnology Center
Office: (765) 494-3036

From: Bnc-facility-notice <bnc-facility-notice-bounces at ecn.purdue.edu<mailto:bnc-facility-notice-bounces at ecn.purdue.edu>> On Behalf Of Voorhis, Mark L.
Sent: Friday, December 18, 2020 6:26 AM
To: bnc-facility-notice at ecn.purdue.edu<mailto:bnc-facility-notice at ecn.purdue.edu>
Subject: [Bnc-facility-notice] NOTICE - East General Lab Wing HVAC Interruption

All,

At 5:30AM this morning a building controls alarm was sent to Purdue trades to investigate the shutdown of AHU 2 that service both first floor and second floor east lab wing (layouts below).  At this time there is higher negative static pressure in all these labs sucking the door to the lab space close.  It may be difficult to open these door when entering these labs.   The temperature and humidity control in these labs will be out of control until we can get AHU 2 operational.

We will keep you posted by email on any changes .


[cid:image001.png at 01D6D528.C6CB03D0]  Frist Floor East Lab Wing

[cid:image002.png at 01D6D528.C6CB03D0]  Second Floor East Lab Wing


Mark Voorhis
Building Manager
Purdue University
Birck Nanotechnology Center
Office: (765) 494-3036


-------------- next part --------------
An HTML attachment was scrubbed...
URL: </ECN/mailman/archives/bnc-facility-notice/attachments/20201218/0e646cd4/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 135189 bytes
Desc: image001.png
URL: </ECN/mailman/archives/bnc-facility-notice/attachments/20201218/0e646cd4/attachment-0002.png>